I was told that oil and water cooled pumps where submursible, while air cooled was not. Mine was Mfg. in 08/02, no idea of when it was installed.
 
Argh!!! My pump just died. I was pricing March pumps. Could I use one of these pondmaster pumps? 16k btu
 
I use the March LC-3CP-MD, 510 GPH. I run it basically 24/7/365, even leave the AC on when my boat is docked behind my house. More than sufficient and has proven to be very relaible ......... so far. :)

Liquid cooled, completely sealed, submersable.

quote:

Originally posted by fastguy91

Argh!!! My pump just died. I was pricing March pumps. Could I use one of these pondmaster pumps? 16k btu




 
Make sure if you have a gas boat the pump meets the USCG standards for ignition protected. Pascal mentioned this earlier but other posters have come into the thread I believe this is important enough to repeat.
Bill
 
I would think if the pump is submersible it wouldnt be a problem. I could be wrong, thats hy I asked. Rnbenton, Are you sure your A/C is only 7k btu? I had an 89 Mariner with a 12k btu and it would get warm in the summer.
 
16,000 BTU AC will require a 600 PUMP. Keep in mind that the 600 GPH (12,000 BYU's = 1 Ton, so you have 1 1/2 Tons) is for level pumping, once you start to "lift" or "longer hose runs" you will need more GPH as the "efficency curve" drops. I would recomend at least 900 GPH. Look up you AC Mfg. on the web, most willhave some detail on pump requirements. Many of the pump Mfg. also have charts that show the drops in GPH based on the length of your run and how high you have to lift from the pump to the condenser.
 