Reverse Air vs. Heat element?

As mentioned above, one good benefit if you winterize and stay on board some in the off season, and boat is kept in a slip, you can use the heat element thru the regular boat air handling system, without having to rig ceramic or other heaters, extension cords, etc. My last boat had the heat element and we were able to stay in comfort all thru the winter down into teens and twenties. Dock mates with RC all had to rig heaters cords etc. How cold does it get where you are, do you stay onboard some thru the offseason?
 
quote:

Originally posted by SLW

Just to clarify, reverse cycle doesn't "work great all the time." Houseboater is correct: most units are rated to produce heat with 40 degree seawater, and can produce heat down to about 35-36 degrees. After that, they blow cold and then go into the "low pressure" warning mode and shutdown.

We've been lucky in our S.E. Michigan boathouses this winter, the water has been warm enough to keep the rev cycles going. At this time last year, we had already put several months of usage on our space heaters.






Are the marine units designed differently than those used in houses?

I have used nothing but nothing but a reverse cyucle unit in my house for the past 29 1/2 years. It works very well in ambient temperatures below 40 degrees and even below 20 degrees.

I have resistance elements that can be turned on if required, but the only time I can remember using them was many years ago when we had the ambient temperature go below 10 degrees.

Why would they design a marine unit to blow cold below 35-36 degrees? Does not make sense to me.

kGeorge
 
Topics kinda gotten splintered... went from a what should i replace with... to using it on the hard....

First the element heater will draw more electric then his current breaker is rated for unless he undersizes the element... that kinda defeats the purpose... so the whole conversation becomes mute.

A heat pump can be used under certain conditions in cold weather with proper controls ... so certain units will work better.

IN GENERAL 35 - 40 degrees is the cutoff . as removing the heat from the ambient air or water becomes more difficult as there isnt much...

But slowing down certain componets ( condensor fans , water pumps etc ) aide in getting more heat.

Rob
 
quote:

Originally posted by Robski97

Topics kinda gotten splintered... went from a what should i replace with... to using it on the hard....

First the element heater will draw more electric then his current breaker is rated for unless he undersizes the element... that kinda defeats the purpose... so the whole conversation becomes mute.

A heat pump can be used under certain conditions in cold weather with proper controls ... so certain units will work better.

IN GENERAL 35 - 40 degrees is the cutoff . as removing the heat from the ambient air or water becomes more difficult as there isnt much...

But slowing down certain componets ( condensor fans , water pumps etc ) aide in getting more heat.

Rob





"A heat pump can be used under certain conditions in cold weather with proper controls"

What do you mean by this statement? I know of no controls needed in addition to what is built into the unit.

You also said "IN GENERAL 35 - 40 degrees is the cutoff . as removing the heat from the ambient air or water becomes more difficult as there isnt much..."

IN GENERAL extracting heat becomes more difficult as the ambient air/water/ground temperature gets lower. Period. It has nothing to do with 35 to 40 degrees. It is more difficelt at 50 degrees than at 55 degrees.

Are you speaking from experience in saying that 35 -40 degrees is the cutoff for useful operation? Maybe you have been used to a very ineffecient unit.

My reverse cycle unit has no discernable problem keeping my house at a comfortable 72 degrees year round. The colder it gets the longer it has to run to provide the same BTU output. The great majority of my neighborss and a large number of the residents of this part of the state rely totally on reverse cycle heating and cooling.

G
 
G, there's a critical difference in the home units vs. marine. Your house heat-pump uses ground water that stays at a constant temp. Seawater on the other hand, varies in temperature tremendously. A Cruise-Air unit is 100% efficient in the heating mode until the water temps goes below 55, and they're rated to produce heat until 40 degrees. As I said earlier, they actually produce a LOT of heat down to 40, and we've seen great performance even below 40. Dometic, the mfr of Cruise Air systems warns that damage can occur if they're run in water temps below 38. So strictly by the rules I guess we've pushed the limits now and then, but as year-round Great Lakes boaters, eh - you do what you have to do sometimes to be comfortable and in our experience it'll shutdown or start blowing cool air before it damages itself.
 
G,
I was speaking in general terms. Most effciency curves for heat pumps are based on 40 degrees... ... I Wasnt being specific.. But ur house unit doesnt apply to a boats heat pump. Water source heat pumps are much more effcient.. but thats not the topic and a preheated house doesnt apply either. A Boats equipment is usually off until the owner comes down. Trying to heat a cabin 0f 40 something degrees with an outside air or water in the low 40's is not going to happen anytime soon.... so were not talking the same stuff....

So whats ur point ? Did u help Billy answer his question... ummm thinking not ... Did u answer anyones question ??? Nope ...

So then stick to the topic ...

Rob
 
quote:

Originally posted by OLD HOUSEBOATER

You have a 1993 boat. HVAC units typicall last the life of the boat or at least 25 years. Did you have your present units back flushed and serviced?? whats the problem with them???






They have been cleaned and flushed. To answer your question I am upgrading almost every system on the boat. My wife hates being cold. I personally don't mind it being on the chilly side. I wasn't impressed with the heat output with 45 degree water (actually "she" my wife wasn't). In my quest to do things one time that is why I asked the question. Someone else mentioned on the hard that is not what or why I asked about RC vs heating elements. I'm leaning towards leave whats not broke alone in this case. I also figured the newer units might be more efficiant than 14 year old technolgy and possible small restrictions that maintenance can't correct. Thanks everyone for your input.
Take care. Bill
 
quote:

Originally posted by Robski97

G,
I was speaking in general terms. Most effciency curves for heat pumps are based on 40 degrees... ... I Wasnt being specific.. But ur house unit doesnt apply to a boats heat pump. Water source heat pumps are much more effcient.. but thats not the topic and a preheated house doesnt apply either. A Boats equipment is usually off until the owner comes down. Trying to heat a cabin 0f 40 something degrees with an outside air or water in the low 40's is not going to happen anytime soon.... so were not talking the same stuff....

So whats ur point ? Did u help Billy answer his question... ummm thinking not ... Did u answer anyones question ??? Nope ...

So then stick to the topic ...

Rob






Rob, even though I do not have your lack of expertise or experience, I hope that I have helped Billy answer his original question.

Home reverse cycle units and those for marine use have much more in common than they have not. I hope that I have helped him see that there really is no such thing as a general or any other mysterious cuttoff point at 35 -40 degrees.

If you do not have personal expertise or experience in using reverse cycle I would suggest that you keep on the sidelines and stop confusing people with your opinions.

G
 
Ok: understand however, that a 12,000 Reverse Cycle unit will put out a LOT more heat with 45 degree water than 5500 BTU heat strips. Check out an installation similar to what you plan on purchasing before you jump in.

Also note that the newer units have less amp draw for the same output. You might consider 13500 BTU units.

Luck
 
Throw'n my .000002 worth in.
Been a little apple to banana comparison done also.

Standard residential heat pumps use NO water from ANYWHERE with the small exception of the melted ice that forms on the condencer and has to be cycled off. They draw heat from the outside ambiant air.

Geothermal heat pumps ( have another name also, cant remember it ) do use liquid, that is circulated through underground piping. These units are much more efficent than the standard model, and on average the underground temp stays above 50 deg.

The BTU/H rating of a heat pump is rated at a temp of 65 deg ambiant, no matter what type. The lower the ambiant temp goes, the less but/h it produces, and at 50 degrees, the btu/h is cut nearly in half on a 3 ton unit. So a 12,000 btu/h heat pump may only produce 5-6000 btu/h at 45 degrees ambiant, which is generally not enough to maintain a comfort level due to the air temp comming from the vents which in ideal conditions is only 90, heat strips are generally 130 no matter the outside ambiant.

So what am I saying, to answer the original poster's question, go get educated, and I will tell you how to answer your own question, the numbers wont lie, and math has no personal bias. First, find out what the lowest water temp on average will be where you are located, when the latest the boat will be in the water. Next, go to your dealer, look at the unit that you are concidering, there will be a load chart either on it or in the information guide, if not, ask the dealer for it. Next find what you comfort level ( or your wifes like in my case ) is, you take these figures and you will find out if this unit will work or not, if the dealer doesn't know how, let me know and I will tell you how to do it, but you will need the load chart from that unit.

actually, saying they will work at 40 degrees water temp is being very generous, most of the manuals that come with them say below 50 may require aux heat.

Personally, to cover all bases, I think you should really try to find a unit with the strips built in that way if the heat pump stops working, you have something to back it up. Even though I live in the south, I have a heat pump, 5 ton, heating 2800sqft, and if the temp hits 40, forget it, might as well turn the ac on, and this is what they do, once you fall below the btu level necessary, and the ambiant air temp, then they cant operate anymore, and you have to supliment it. Good luck....D........
 
George, please re-read my earlier post. There is ABSOLUTELY a cut-off 35-40 degrees. I've said it, Arks said it, Capt Ed said it, and Rob has said it. It' also in the documentation provided by at least one manufacturer. I'm speaking from personal experience, as my boat is sitting in 30-something degree water RIGHT NOW (as it will for the rest of the winter, and as it did the winter before this...)

Rob has been known to show some temper, and at this point, it's justified!
 
When I was looking at ac units I considered the heating elements just because I stay on the boat in the spring when I am getting it ready to go in. But after comparing the heating elements and revers cycle I found that the reverse cycle was better because I would never be in the water when it was below 40. As many times as I stay on the boat out of water I could use a small heater for that. I have a friend that has the heating elements and wishes he had reverse cycle after being on my boat.
 
D,
Geo thermal = water source heat pump. think thats the name u were looking for....

SLW... thanx ...

Rob
 
funny thing about reverse cycle is when conditions are toughest the air coming out may feel cool even though it is warmer than the area. Home units have optional heat strips Do any marine units give you the same option?
 
Bruce, I know cruse-air offers a element module for thier units ranging from 1 to 5 ( I think ) kw depending on voltage available, you can get higher kw units if using either 220 or 3 phase, if I remember right you max at like 4kw on 110, with a load rating of 18 amps, and is supposed to be a plug and play type for the controller, just have to run the circut for it.

Rob, there is another techinical name for the geo thermal units, with the marine units fall under that also, I will think of it later, you don't see those types around here............D........
 
I did some research with Marine Air. Their units are rated at 45 degrees and 100 degrees condenser temperature. Since you don't get into water temperature over 100 degrees you always have rated cooling out put. You do, however, get in water under 45 degrees, heating efficiency can fall off in excess of 30% in these situations. IMHO Still better than heat strips.

Note: When you sell, your buyer will expect reverse cycle.
 