AC Water Drain Issue

LuBell

Member
Joined
Aug 1, 2008
RO Number
30482
Messages
65
Water is coming from the AC on my 1990 Carver 3257. Because all the hoses and connections are intact, Im assuming that it is condensation. Only with the unit on, water accumulates in a shallow pan underneath the condenser. It then overflows into the bulge, wetting the wood that houses the unit. Theres got to be a drain for this pan that might be clogged, but I can't find it. Any ideas about any of this?
 
There should be a hose from the drain pain to either the bilge or the shower pump. When the drain hole/hose gets clogged, it will overflow.

Find the hose and run a wire through it to clear it.
 
quote:

Originally posted by HOGAN

There should be a hose from the drain pain to either the bilge or the shower pump. When the drain hole/hose gets clogged, it will overflow.

Find the hose and run a wire through it to clear it.






Then pour some chlorine bleach through it.

If you are going to be away for a week and the HVAC will be running, put a drinking water chlorine tab in the pan to aid in killing any thing that may be growing in there. Leave a hatch open for venting.

HTH.
 
Just look at the unit and think to yourself " where is the worst possible place be for the drain to be located?" Then you'll find it.
 
quote:

Originally posted by HOGAN

There should be a hose from the drain pain to either the bilge or the shower pump.





Or, directly overboard if the unit is mounted above the waterline.

You will have to inspect your boat and find the line, then clean it out. If you can't find it, get some help.
 
I use a venturi device on each of my AC units diacharge side. Recently the front AC unit started to overflow and smell. The one way check valve had to be cleaned. I did both AC units. This system drectly discharges the water into the AC cooling water thru hull (above the waterline).
Now it's just another item to add to the routine maintenence list.
Bill
 
I just had this fixed on a new boat, the technician told me there were fuses associated with the pump that were not installed. If you don't find a clogged line you might look for some blown fuses.
 
The idiots who fixed my shower sump, connected the a/c condensation line to the output side of the sump. . . of course there was no where for the water to go, and it took us 2 years to figure why we were always getting water in the bilge. Your problem is most likely a clogged line - but check the shower sump anyway . . .
 