Battery Isolator vs. Relay

HarlenW

Member
Member
Joined
Mar 30, 2007
RO Number
25699
Messages
473
A friend of mine is thinking about changing out the battery isolators that came with his boat, a 2006 Mainship 34 Trawler, with battery relays. He has three battery banks, house, engine and thrusters. He was told by a salesperson that battery isolators are obsolete and that they drain 1 to 2 volts of DC electricity from the charging system.

Is there any downside to this?

Thanks.
 
Downside to what?

In any event I'll go over the discussion, as I see it.

Only known ( to me ) downside to a combiner ( "relay type" ) is the possibility of a failure in the closed circuit condition. Not very likely, and I have never heard of one doing so.

Isolators work using diodes, which cause a 0.7 to 1.2 volt drop, depending on the diode. When wired correctly, this is compensated for by the alternator ( using the sense wire ). It does, however cause the alternator to operate at a slightly higher voltage. The upside is that if an isolator fails, it fails in the "open circuit" condition, ie: fail safe.

SO, properly installed, there is little difference between the two; the batteries are charged just as well w/ isolators as w/ combiners.

The salesperson has formed an inaccurate conclusion, based on incomplete knowledge. Installed correctly, both systems work flawlessly.

--

That said, I have used both systems. Isolators and their critical wiring are confusing to most mechanics, and this confusion can cause problems. As a result of this, I switched to combiners and achieved good results with them. Good results were had with the isolators, except for the issue with the mechanics!
 
"The salesperson has formed an inaccurate conclusion, based on incomplete knowledge. Installed correctly, both systems work flawlessly."

One of the many reasons why I don't believe what a salesman says! I find they usually little about boats except all the tricky sales techniques to try to sucker you in and "upsell"!
 
I have read about combiners and they make a lot of sense. In a boat with just a house and a starting battery does a combiner actually replace the battery switch or work in conjunction with same?
 
The short answer is that is replaces the switch. ( at least, the switching function )

But even with a combiner, it is appropriate that each battery have a cut-off switch. When adding a combiner/isolator, you normally have a nice switch "left over", which can be used as a battery cut-off switch. Or you could use a new (On/Off) only switch. Which is up to you.
 
I use a combination of manual battery switches (cut-off) and manual switches on the charging lines (AC smart charger or output from the solar controller) for a three bank set-up. This is not an automatic system, but it works.
 
The best Dc systems IMHO use combiners.

I've had the best luck with them, no switching involved, very reliable.
 
If your going to use true relays and not combiners make sure they are constant duty DC relays. Blue Sea makes one part # PN9012. Many boats have an emergemncy start relay they are usually only for short duration use.
 
Combiners are the best solution but at the time I did the wiring I wanted to save a couple of hundred. Switching is fine as long as you remember to do the switching.
 
...and it's important to have the 'make before break' type switch if you switch while the engine(alt) is running or you may burn out the diodes in the alt.
 
Back to the isolators vs the relay. A lot depends on the type of alternator you have. The diodes in an isolator DO cost you maybe a volt. However if the alternator has a separate "sense" wire (three wire alternator) you run the sense to one of the BAT posts on the isolator. The alternator will then read the actual voltage at the battery (beyond the diodes), and step up the charging voltage to compensate for the loss. If you have a "one wire" alternator you can't do this, so in that case you'd get a better charge with the relay.

On a new installation I'd go with the relay, but I wouldn't go to the expense of changing over just because the old system was "obsolete". If it works, why "fix" it???
 
With a multi-battery setup the sense wire can only go to one battery leaving the others potentially discharged. I used to be an isolator fan but had lots of annoying issues. Switched to combiners after Robyns Nest pointed me to the light several years ago and haven't looked back since.

Much more reliable and my batteries stay very happy.
 
There's a way around the sense wire issue. IMO it should be on whichever battery tends to be lowest; this will keep the charging current up to all of them. I used to have the sense wire on the house batteries, but since I upgraded my solar system they're usually fully charged, so I switched it to the starting battery. In either case the isolator will send most of the current to the lower battery, but if the alternator is sensing a fully charged battery it'll reduce output. Yes it can be problematic.

The combiner has a definite advantage if you have a "single bank" battery charger or a solar system (my case). There is no sense wire so you have to connect the output directly to one battery or the other, and the one NOT connected doesn't get a charge. If you connect it to an isolator you'll lose that volt and won't get a full charge to either battery.
 
I installed a combiner several years ago and am pleased with it. However I do have a question about the impact of continuing to charge a fully charged battery bank. I have a house bank and two starting batteries connected via a combiner. The starting batteries are likely fully recharged after only a few minutes underway. However the house bank may be discharged and recharged several times each day. Does this impact the starting batteries? They do seem to need water more often than the house batteries.

Thanks, Ted
 
I'm NOT an expert but it's my thought that once the battery reaches the required voltage the relay closes and allows the current to go to the other battery. However I have a feeling that the alternator "sees" the fully charged battery and reduces output accordingly; so the current to the second battery would therefore be reduced. You might try connecting the alternator output to the house batteries so they would get charged first, but there might be a risk of not charging the start batteries at all.

With an isolator I think the current takes the path of least resistance so would go to the lowest-charged battery first, till it comes up to the level of the more fully-charged battery. Then they'd come up together.

There are so many variables involved I can't determine a "best" hookup. Maybe someone else can.
 
quote:

Originally posted by Ted Williams

I installed a combiner several years ago and am pleased with it. However I do have a question about the impact of continuing to charge a fully charged battery bank. I have a house bank and two starting batteries connected via a combiner. The starting batteries are likely fully recharged after only a few minutes underway. However the house bank may be discharged and recharged several times each day. Does this impact the starting batteries? They do seem to need water more often than the house batteries.

Thanks, Ted






Once one bank on the combiner reaches it threshold voltage, it combines all the banks so that the charge can pass to the the bank that is at the lower limit. It doesn't disconnect banks until the voltage on one of the banks drops to a preset voltage, thus saving the bank from total discharge.

Isolators are old technology and really shouldn't be considered if you want the best setup.
 