I don't have a generator on my boat, but would like one on the next one. I was reading on another board about generator use and also deaths. I was surprised how many deaths or severe CO Poisonings have occurred due to generators running while the AC is going. Most of which sound like permanent units, not portables. Pretty scary report.

http://www.doubleangel.org/documents/NatlCaseListingBoat-RelatedCOPoisoningsMay2007April2008.pdf

I thought it was common practice to run a generator to keep the AC going at night. It sounds like this is a big no no. When many of you go out and raft up, do you keep them running?

Can someone explain the proper use of a generator? Also if you don't leave it running all night, are there other ways to keep cool while on the hook?

What does a low CO or CO free generator cost? It sounds like it would be worth the investment.

MJK
 
quote:

Originally posted by king5899






King,

We run ours all night quite often in the summer when on the hook.

We keep it tuned up and check all exaust connections frequently.

Our cabin has a built in CO detector / alarm, and I also purchased a separate battery operated one from Home Depot as a backup.

If the temp is OK at night, I'll leave it off, but that is rare here (Charlotte, NC) in the summer.

If you take proper precautions, running it at night is OK. Test the CO detector(s) just before you go to bed.

I also usually set a little alarm clock to get up once during the night and look around, check the weather, bilge pump, drift, Generator, etc.

We only anchor from the bow at night. Assuming your generator is in the stern area, the wind will always blow the fumes away from the cabin vents.

Be a little more suspect of CO if there is ZERO wind.
 
First: my bias. I'm paranoid, because they really are out to get me.

--

Yup. Those statistics are accurate ( as far as they go ). ANYthing that burns a fuel can produce noxious by-products, however, by using good maintenance, and taking precautions, the risk can be reduced. Diesel generators do produce CO, but much less, compared to a gasoline generator, so part one is either use a diesel, or get -real- paranoid.

Next: Use CO monitors. Note the plural. They are not foolproof, but should help avoid most problems ( I'd guess over 90% or more )

Next: Be careful about genny maintenance.

Next: be careful about where the exhaust and fresh air come and go. Make sure that you are breathing fresh...

Next: Many genny users actually cool down the boat, then shut down both the genny and the A/C. This avoids the risk, and quiets the system, which is easier on those aboard, as well as helping keep happy neighbors.

Next: Some use the inverter to operate the A/C overnight. This is usually a major usage, and not all boats are properly equipped to do this. But if you are, you get safety, quiet and cool.

That should start the debate... :)
 
there are a few basic precautions you need to take with a genny...

-anchor from the bow only so wind will push the CO away from the boat
-have at least TWO CO detectors on board
-be careful when anchored in a current as the current will make the boat lay at an angle to the wind
-some boat are better ventilated and actually comfortable most of the year
-I dont' agree that running AC on inverter in practical but an inverter will allow you to use large 110v fans which will keep you cool at night 95% of the time, as long as you have goo ventilation.
-consider a diesel boat (diesel emits very little CO) or a boat with a low CO gas genny

Rant: modern boats have very poor ventilation so wihtout AC it's game over. I dont' get it... well i do... opening windows cost more especially if you dont' want them to leak although the problem exist even on large multimillion sportfish and MYs. what a shame... even here in So Fl summer, there is usually enough breeze to keep the saloon cool during the day since air comes in thru side windows and side doors.

about the report, good information and a must read for any boater... BUT.. in all fairness, many death or injuries on BOATS not houseboats occured from the main engines, not from the generator. Houseboats are a different stories since by design they tend to trap CO. Also, on lakes, beaching or tying to shore is more common which means the boat doens't point into the wind.

it's all about common sense.
 
Like Airbus, when we had our SeaRay 290 on Lake Norman, we ran the generator all night. I'm a light sleeper on the boat, so I was up once or twice checking things, etc. The key is anchoring from the bow and allowing the boat to swing. The yacht club we were a member at frequently had raft ups, the rule was generators off at 10pm, if you wanted to run the generator you split from the raft up, on a hot night that's what we did. This was not only for noise, but in a raft up of 5-6+ boats, they are not going to swing in the wind, thus it is more likely co could make it's way into the cabins. I think you are more likely to encounter co poisoning swimming around the generator exhaust or from the station wagon effect of the boats propulsion engines when running with canvas up rather than having it work its way into the cabin from a running generator. All three scenarios pose a risk. Unfortunately, many poisonings occur in a rental situation with a houseboat and the renter had no idea there was any risk in running the generator.
 
quote:

Originally posted by PascalG

there are a few basic precautions you need to take with a genny...

-anchor from the bow only so wind will push the CO away from the boat
-have at least TWO CO detectors on board
-be careful when anchored in a current as the current will make the boat lay at an angle to the wind
-avoid rafting up with gensets running, the more boats the more risky
-some boat are better ventilated and actually comfortable most of the year
-I dont' agree that running AC on inverter in practical but an inverter will allow you to use large 110v fans which will keep you cool at night 95% of the time, as long as you have goo ventilation.
-consider a diesel boat (diesel emits very little CO) or a boat with a low CO gas genny

Rant: modern boats have very poor ventilation so wihtout AC it's game over. I dont' get it... well i do... opening windows cost more especially if you dont' want them to leak although the problem exist even on large multimillion sportfish and MYs. what a shame... even here in So Fl summer, there is usually enough breeze to keep the saloon cool during the day since air comes in thru side windows and side doors.

about the report, good information and a must read for any boater... BUT.. in all fairness, many death or injuries on BOATS not houseboats occured from the main engines, not from the generator. Houseboats are a different stories since by design they tend to trap CO. Also, on lakes, beaching or tying to shore is more common which means the boat doens't point into the wind.

it's all about common sense.




 
We run the genny for about 2 hrs before we go to bed and use the ac to cool down the boat as cold as we can get it. We leave a window or two open and never get warm until morning. We did this last summer on a couple of hot nights and were fine. If you have any doubts ask yourself one question. Is it worth it?
 
It needs to be said that it is not enough to take all of those precautions with your own boat. There have been several deaths from CO coming from neiboring boats, especially in a raft-up. They are out to get me too!
 
On hot muggy nights here on Long Island, we run the AC for a couple of hours before turning in. Then we shut it off when we go to sleep. As much as I hate the heat, I wouldn't sleep well thinking about the CO. We have two CO detectors in the cabin, and our friends have no problems sleeping with their genny running all night. I'd rather be safe than sorry.
 
We run it 24/7 in the summer. It is way too hot for us not to.
When the sun hits the top of the cabin, the heat radiates into the cabin.
Opening the windows and hatches doesn't seem to help.
If we are just running around for a few hours just to ride, we don't run it.
We have 2 CO detectors and they seldom give us any alarms.
Only in a July 4th raft up(once) and 1 other time when running the boat with the wind,
generator shut down, doors open but not windows and hatches.
 
quote:

Originally posted by airbus

quote:

Originally posted by king5899






Test the CO detector(s) just before you go to bed.







Just pressing in the test button, on most CO detectors, ONLY tests the buzzer. It does not test the ability of the CO detector to detect CO.

From the same "other board" mentioned in the OP, among other good information, I took with me a few key pieces of information.

- Have multiple CO detectors powered from different sources...AC..DC...Different DC banks...Different AC circuits...etc..

- Install CO detectors in your cockpit.

- Replace your CO detectors every 2-3 years...REGARDGLESS....they have a life expectancy.

- VENT, VENT, VENT....
 
We had a 120 vac CO detector and a battery powered one.
The 120 vac unit died this past summer.
It was great to have it as a back up.
The battery one ran all the time and the 120 vac unit ran when
we were plugged in or when we were running the generator.
 
Did anybody notice that a large portion of deaths were on houseboats with extended unvented swim platforms?
 
To those who get up in the middle of the night to check for problems:

If you are under the influence of CO, you will not wake up regardless. CO decreases the oxygen in your blood which in turn makes you go to sleep. Do not count on saving yourself and/or others on the boat with an alarm clock.

Personally, I would not want a generator onboard. Nor AC. When it is hot, I run oscillating fans to get some relief.
 
Please dont jump all over me I know nothing about propane........ I saw a portable propane powered generator last week. Do propane generators still generate lethal unhealthy levels of CO ?
 
Propane does not put out near as much CO as gas.
That is why you see propane lifts and fork lifts inside stores.
But they do put out small amounts.
 
It also amazing to see the number of incidents with people getting co poisoning because they were in the water or sitting on the swim plaform with the propulsion engine running. Specially the one with the guy who had his 3 girls riding on the swim platform as he was going through a no-wake zone. No common sense at all.
 
Separate those deaths from in the water or on the swim platform (teak surfing) vs those inside of the cabin. This is an excellent summary.

CO detectors rely on a chemical reaction and the units should be replaced every 2 to 3 years as noted above. The Kiddie Night Hawk is battery powered, and has a digital read out and is an excellent unit. The best unit is the AeroMedix--but this is more expensive and made for airplane cockpits. CO is cummulative and will build up in the blood stream if exposed over peroid of time.

Personally we have two CO detectors. We have one at the helm and one by our heads in the bunk. We run the AC unit to cool the boat down, but then shut it off when going to bed. If we wake up, we open the hatches, and turn on the fans (including a O2 (wal mart for $15, 12 volt or D bat) or Endless Breeze in the hatch, plus individual fans for each of us.

We sailed many years in the Caribbean and Mexico without airconditioning. We had good ventillation in our sailboats, and a wind scoop, which brought breeze thru the hatchs. You can acclimate to the heat if you will take the time....but some "sweat" is involved.
 
We have run ours all night. I have the newest Kohler 7.3ECD Low CO unit, with the optional salon control head and sensor. This generator has a catalytic converter. The genset will turn itself off if the Kohler Salon detector detects CO if the detector is out of specifications it will show a code and still turn the generator off. The only way to bypass this in an emergency is to unplug the remote from the genset and clear the code on the digital panel on the genset and then restart it at the genset. I think this is a great idea by Kohler and they probably did it to limit product liability. In addition I have a Xintex fume system with 1 sensor under the cockpit and the other near the bulkhead under the salon for near the AC units intake. In addition I have all 3 year old Xintex 12VDC detectors in every room in the boat. Then up under the hardtop at the bridge I have another Xintex CO detector hard wired and a ceiling mounted battery powered CO detector that is one season old. Do I feel safe? I feel uneasy I always crack the bow window for fresh air. Most of the time we do what has been mentioned above run it and get the boat as cool as possible and turn it off and go to sleep. Then we run 2 12volt DC fans. Bill
 