Is it possible to recharge the freon level in a reverse cycle AC unit myself? If so, how is the process done and where can I buy the freon? Thanks.
 
yes you need gauges may need license to buy freon need to know what type of freon and if its low need to figure out why as sealed unit dosnt usually require freon. there maybe other reason for poor performance . ie water flow dirty condensor
 
You could IF you could buy the freon, however if you are not a certified ac man that no one will sell it to you, it's the law. Just call and have an ac guy check your unit, a check out with a bit of freon should run you $100-150

Cor
 
An AC doesn't "use up" the freon, the only way it gets out is if there is a leak. So even if you could recharge it, it will leak out again unless you find the cause.
 
Family time post what the problem is with the unit .. IN DETAIL... Im sure we can point u in the right direction.

Rob
 
The problem is with freezing up. I get a block of ice on the coil when I set the temp at 70 or lower on a hot humid day. Thanks.
 
Definately get an A/c person to check it out. Recharging could only be temporary and not necessarily the root of the problem.
 
Usually just read posts, have learned alot on this forum. Since I am an a/c man thought i would reply. If the unit freezes up rather quikly than probibly the charge. If takes awhile than maybe airflow or combination airflow and cold water through condenser causeing low pressures( probibly not since you said hot humid day). Make sure no are grills closed, coil is clean and fan blowing strong. a/c units are not designed to maintain 70 or below, especially on very hot humid days. But still should be able to run continuosly without freezup. If still problem must call for service as will need leak checked before recharged.
 
quote:

Originally posted by Family Time II

The problem is with freezing up. I get a block of ice on the coil when I set the temp at 70 or lower on a hot humid day. Thanks.






I'm not sure how marine's a/c system works but if it's anything like on Automotive and your system is freezed up, it's not a low freon problem, it's more likely either restriction on air flow to condensor and or bad/stuck expansion valve that will causes an external freezed up, best way to diagnose the problem is hooking up a manifold gauge set and see what the reading are on both side.
 
Is the coil fully frozen top to bottom or is it only frozen on one side?

How fast before the unit starts to freeze up. ( this is important )

If u feel the evaporator coil is the temperature of the coil consistant top to bottom.

LEt me know

Rob

DVA there is no expansion vlave on these .
 
The unit will run for hours before freeze up. When it freezes, the entire coil, and at times if the unit was running long enough, the canister of the unit is also frozen. Could it be that the coil is dirty? If so, how do I clean it? Thanks.
 
Well honestly its a tough call... if it is short on gas its very slight.... but then again the unit only has onces to begin with. The coil could be dirty ... the factthat it takes so longto ice up and ices top to bottom kinda points to dirty coil.... so easiest thing to do is use some compressed air to blow out the coil. Water is not a option.... I dont know ur setup but we dont want water laying in the fan shroud housing. ( mold mildew ) So clean it ....then we reevaluate it

Rob

Need more help email me first**nyc.rr.com
 
Good to know there's no Expansion valve on the marine air system but how about the Orifice tube?. There has to be something in the line/pipe/tube to convert the gas/liquid.
 
Do eveything you can yourself first. Be sure the coils and vents are clean, that all ducting is intact, and there's no "short cycling" of discharged cold air right back into the warm air return.

Yep, capillary tube. Just went through this, friend had a blocked cap tube in one and sent out to somebody who could force it open using high pressure oil. Worked, but I wouldn't call it a total success.

Rob, could it be cleaned with water then the water pulled out with a wet/dry vacuum? GAS FREE BILGE CONCERNS APPLY HERE!
 
Do the easy things first and like others have suggested, I would check air flow first. Find the return vent and pull the filter. Make sure the filter is absolutely clean.
 
J-D,
Problem is there is no hole in the housing to drain the water. It wouldnt normally be there so they never plan for it ... plus air would leak from it and other issues develop.. If access is easy just unplug her , disconnect the water lines and ur good to go to put her on a bench.
( 2 or 4 clamps hold the entire a/c skid in place. )

CO2 would be the 2nd best alternative to water... just control the pressure and dont bend the fins... then we'd be really hosed.

Air pressure out of the supply vents should be noted. Another thing i just thought of ... the return air sensor has to be mounted to the evaporator ..if it became detached that would be bad. it has two wires and has a small thermistor in the end. ( metal cylinder or may be dipped in plastic which is bad but they do it )

Rob
 
CO2?? Why not compressed air or nitrogen to blow the coil out. If was a restriction in cap tube would freezup fast just like if low on gas. If not airflow you need a/c man.
 
quote:

Originally posted by Robski97

so easiest thing to do is use some compressed air to blow out the coil. Water is not a option....






I am really confused, what are you guys talking about?

The coils that I thought we are talking about here are the evaporator coils. They will have a large amount of water condensing on them during normal operation, I fail to see how using water to clean them would be a problem. Due to the condensation the AC unit must have a way of removing the water, often into a sump pump for discharge overboard.

I would be very careful about using pressure anything (air, gas or water) to clean the coils. A direct blast of high pressure can bend the fins and make a bad situation worse.

Rod
 