I have some black electrical tape if you need it.
 
We don't have shore breakers, just an on off switch...... Is it the norm to have a shore breaker?

Walter
 
you dont have to be overloaded to cause a fire a little resistance and you get what you got. it happens frequently. Dont look for complicated probelms when simple answer is common.
 
W.

You mayhave hada loose or corroded connection in the receptcial itself. Very common on 30 amp. In over 45 years of boating I have replaced a lot of cord ends and a half dozen recepticals. I've been the dock handyman all my life.
 
The type of failure described will not normally trip a magnetic or heater type breaker. Arc-fault breakers
were developed, and now required by elect. codes in residential use, to protect against this type of
failure.

http://www.geindustrial.com/publibrary/checkout/38652.30055.10569.48080/HTML/afci_paper.htm

The above web site will tell you all you want to know and more about this issue and the breakers
developed to address the problem.

All the major companies involved in supplying breakers now make AFCIs.

Pete
 
Bay......I think the AFCI breaker regulation was dropped from the National Electric Code last year.

Walter...... You should have a 30 amp breaker at the power tower......to protect the boat. Most towers have a non GFCI 30amp receptical and a 20amp GFCI protected receptical.
 
Don,

You mean they changed the rules *again* !!! Can't hardly keep up anymore!

Why the change?

Thanks,
Pete
 
If you have a copy of Boatowner's Mechanical and Electrical Manual by Calder, look up Shorepower and loose neutrals-- page 148 in the Third Ed. As several have pointed out - circuit breakers and/or fuses provide no protection for this kind of problem.
 
Bay....... Yeah they change like the wind.....

Originally...(in 2005)....the AFCI ( arc fault current interupter ) circuit was intended to protect bedroom circuits....much like GFCI's do kitchens/baths. The problem was the use of extenshion cords under rugs and beds causing electrical fires. The AFCI circuit had to also be a dedicated home run for each/every bedroom in new construction....which could get to be real expensive. The AFCI breaker (should) open when it senses an "arc".....not like a GFCI ( ground fault current interupter ) that opens when the ground is compromised.

The reason it's no longer being enforced is a good question...... but this past year or so the electrical inspectors have not looked for any AFCI circuits wired-in on our ruff-in inspections ...just GFCI's ( back to the 2002 code book)....they say its no longer required....... go figure.
 
Walter, you raise a good question about insurance coverage. My policy spells out a "layup period" between Dec and March. My understanding of layup means more than just being out of the water. I'm not to be spending nights on my boat with a heater plugged in. No coverage there for me. Check with your insurance agent.
Greg
 
I had this happen last year. The connections in the Marinco outlet were loose and corroded. This created heat
which melted the marinco outlet and wires. The old timers on the dock said to use an anti corrosion paste
on the connections. I found this paste at the local electrical supply busines.

I would have guessed that the breaker would have tripped before the plug melted. In my case, the
loose fitting melted the outlet first.
 
Walter...... One way to solve this problem....is to ( next year) run 2 seperate 30 amp cords. One you can plug into the deck fitting....for your normal cabin needs. The second cord you can run into the engine room....just for the engine room heaters. This will split the load and reduce the amps on one single cord.

Then if you want to get fancy.......add a second deck fitting ( somewhere nice ) wired-up to a breaker panel....just for the engine room needs.

I run a secound cord for my engine room on my boat.........works well.
 
I think Walter has a Silverton and they already have 2-30 amp shorepower inputs. Load management is done at the main breaker panel.
 
...Then he would add a 3rd deck fitting.....just for the engine room load.
 
Don,
I was only pulling 15 amps or so max through a 30 amp circuit. I had nothing else on except for the heaters.
So pulling another cord may make me feel better, but it really would not be any different.

Walter
 
My boat is on the same row as Walter's, he could of burned the whole row and the fuel station is right near me too!

I think this is from the heaters. They draw alot and cause the wires to get hot. I don't think any space heater should ever be operated without supervision and I don't think anyone should be allowed to have them on their boats. Too many fires from these heaters.
 
Had the same issue about 5 years ago. Filled the whole boat with smoke, but nothing caught on fire. It melted down behind the inlet.

IMG00006.jpg
 
Thanks for the info Don. I was wondering if the price was an issue. Funny how that works!

Back to Walters problem. Other than rigorous maintenence to prevent such an occurance, the
only breaker that would detect such a failure would be an AFCI, right?

Thanks,
Pete
 
Returns don't burn because they split the load with the ground. Most grounds (that are effective) actually run to the same buss as the neutral.
Bad news Walter. Hopefully you get repaired and back online without too much difficulty.
 